I am looking for the rationale behind 240.21(b) where the code states that the provisions of 240.4(b) will not be applicable.
Here is a scenario:
400 amp overcurrent device feeding 500kcmil copper conductors at 75 degrees C. A tap is made to these conductors with 4/0 aluminum at 75 degrees (the tap rules are followed with respect to conductor lenght).
It is permissible to protect the 500kcmil conductors at 400 amps (the load is less than 380 amps) utilizing 240.4(b) but the 4/0 aluminum conductors would have to terminate in an overcurrent device rated at 175 amps even though if the same 4/0 conductors were fed directly from a breaker the breaker could be rated at 200 amps (with respect to load).
Would the 500kcmil conductors also be considered a tap? I don't think they would, by definition, but why wouldn't the same logic that allows the 500kcmil conductors to be protected above their rated ampacity be allowed for the 4/0 conductors in the scenario above considering it would be permissible to protect the 4/0 at 200 amps if the 4/0 conductors were not, by definition, a tap conductor?
Here is a scenario:
400 amp overcurrent device feeding 500kcmil copper conductors at 75 degrees C. A tap is made to these conductors with 4/0 aluminum at 75 degrees (the tap rules are followed with respect to conductor lenght).
It is permissible to protect the 500kcmil conductors at 400 amps (the load is less than 380 amps) utilizing 240.4(b) but the 4/0 aluminum conductors would have to terminate in an overcurrent device rated at 175 amps even though if the same 4/0 conductors were fed directly from a breaker the breaker could be rated at 200 amps (with respect to load).
Would the 500kcmil conductors also be considered a tap? I don't think they would, by definition, but why wouldn't the same logic that allows the 500kcmil conductors to be protected above their rated ampacity be allowed for the 4/0 conductors in the scenario above considering it would be permissible to protect the 4/0 at 200 amps if the 4/0 conductors were not, by definition, a tap conductor?