Re: Tap Conductors
(1) Taps Not Over 3 m (10 ft) Long. Where the length of the tap conductors does not exceed 3 m (10 ft) and the tap conductors comply with all of the following:
(1) The ampacity of the tap conductors is
a. Not less than the combined computed loads on the circuits supplied by the tap conductors, and
b. Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent-protective device at the termination of the tap conductors.
"B" seems to imply that an overcurrent device will be installed at the termination point of tap conductor. Another wording issue in the NEC. Personally, I would agree that this installation, without the mains, does not meet the "intent" of the code even if it does meet the letter of the code. After this job is complete, what would prevent me from installing say, for sake of arguement, 800 amps worth of branch breakers in one panelboard? Would this not put the integrity of the 400 amp tap conductor in serious jeopardy?
Had a lttle time this AM so looked up some code articles. 408-16, A & B require an OCD noy greater than the rating of the panelboard. That is the section of NEC that would be a violation.