Tap conductors

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows from 200A breaker 3/0 AWG FDR one to 15A fused disconnect and to 20A fused disconnect. Load side of the disconnects are FDR #2. Are FDR #2 two tap conductors?
 

Attachments

  • 62D0A357-B1F6-493C-8BC9-623308572E88.jpeg
    62D0A357-B1F6-493C-8BC9-623308572E88.jpeg
    273.8 KB · Views: 20

bwat

EE
Location
NC
Occupation
EE
Why would you think they are taps if they are protected at their ampacity by the fused disconnect?

240.2 Definitions
Tap Conductor. A conductor, other than a service conductor,
that has overcurrent protection ahead of its point of supply
that exceeds the value permitted for similar conductors that
are protected as described elsewhere in 240.4.
 