Rpack22
Member
- Location
- Santa Barbara
- Occupation
- Electrician
Currently doing a job at a middle school where the electrical engineer has listed taps from a 100 amp breaker from a MSB. Load is 3 different condensing units all fed from their own disconnects, one alone on a 40 amp ocpd, the other two (50A and 40A MOP) are being tapped off of a 100 amp breaker. The EE has listed that #6s shall be used for the tap conductors and it shall not exceed 10 feet. In my mind this is wrong because the total calculated load is 90A (240.21(1)(a)) there for if it’s under 10 feet of tap conductor the wire would have to be sized to 90A. If it were over 25 feet, it could be sized according to their respective disconnecting fuses (50A and 40A).
The way I see it being done is; feeders are #3, tap conductors not over 25 feet but over 10’ are #6 for 50 amp fuses and #8 for 40 amp fuses landing in their respective disconnects. Does this sound about right?
The way I see it being done is; feeders are #3, tap conductors not over 25 feet but over 10’ are #6 for 50 amp fuses and #8 for 40 amp fuses landing in their respective disconnects. Does this sound about right?