Leave us do not allow ourselves to permit "language" to get in the way of "communication." We are using the word "tap" in two different scenarios. Article 240 has a definition of "tap conductors" that only applies to that article. That definition could not apply to (I will avoid the use of the word "tap" for the moment) a "connection" ahead of a service main OCPD or ahead of a generator system's first OCPD. That is because the definition of "tap conductor" says that there is an OCPD upstream, but it is rated higher than the ampacity of the tap conductors. For the fire pump, there is no OCPD ahead of the "tap point," so the conductors are not "tap conductors." QED