An electrical contractor, as an afterthought, wants to tap (hard wire) the 1200 amp factory switchboard after the utility metering section, but before the 1200 amp main disconnect for fire pumps. He desires to make this tap with a 200 amp (3/0 copper conductor) circuit. (200 + 1200 = 1400 amp?). Internally in our company we state the customer must meet or exceed his main disconnect. For multiple main situations contained in a single bussed enclosure, the customer must meet or exceed the main buss rating only, not the sum total of the disconnects acceptable by the 6 switch rule.
What am I missing or not reading correctly in the NEC? Would fire pumps be an exception because of intent to run until the pump is purposely shut down, or the pump itself is destroyed?