I receive an RFI , about tapping from existing service.
am tapping from existing main service to a 400A disconnect to feed a separated building in a 4"C.
according to the contractor, there is no way entering the existing main service with a new 4"C due to troughing on the top and side of the main switch.
there is very little room to safely tap the existing wires, gutter space is limited.
what can be done? any recommendations will be appreciated.
 
Fairly vague on the details to offer specific advice. What size is the existing service? What kind of service equipment (safety switch, panelboard, switchboard). Generally your options include, replacin g or adding lugs to the existing equipment, putting a splice box in, tapping the conductors with some sort of connector.....
 

mepengineer

Member
Location
New York, NY
Fairly vague on the details to offer specific advice. What size is the existing service? What kind of service equipment (safety switch, panelboard, switchboard). Generally your options include, replacin g or adding lugs to the existing equipment, putting a splice box in, tapping the conductors with some sort of connector.....


existing 800A service, the tap is a 400A service disconnet to a DP panel.

my thought was to extend the bus at the existing service CT cabinet and have the tap there
 

drktmplr12

Senior Member
Location
South Florida
Occupation
Electrical Engineer
existing 800A service, the tap is a 400A service disconnet to a DP panel.

my thought was to extend the bus at the existing service CT cabinet and have the tap there

there isn't enough detail here, a picture of the location in question and a one-line would be helpful.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent

OK, so I am betting there is a solution to your problem here, but assuming the contractor is competent, I doubt the best solution is going to be obvious without far more detail. We can't tell means and methods from you picture. We can't see the space available within 10 feet of the splice point for the disconnect. What should be worst case would be run new conduit and wire from the CT cabinet to the existing disconnect through a junction box or gutter and tap in the junction box. Then try to improve from there.
 

victor.cherkashi

Senior Member
Location
NYC, NY
Looking at the drawing the #1/0 EGC in the raceway is incorrect.

(I assume you refer to the tap sizing, not the wire to water service)
Do you mean that #1/0 EGC doesn't participate in tap?
(OR) Do you think that Rating Overcurrent Device in Circuit Ahead is higher than 800A, in this case #1/0 is not enough.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
(I assume you refer to the tap sizing, not the wire to water service)
Do you mean that #1/0 EGC doesn't participate in tap?
(OR) Do you think that Rating Overcurrent Device in Circuit Ahead is higher than 800A, in this case #1/0 is not enough.

There is no EGC on the line side of the service disconnect. The drawing shows 4-500's and a #1/0 "ground" there should be no #1/0 EGC in that raceway with the service entrance conductors.
 

victor.cherkashi

Senior Member
Location
NYC, NY
I receive an RFI , about tapping from existing service.
am tapping from existing main service to a 400A disconnect to feed a separated building in a 4"C.
according to the contractor, there is no way entering the existing main service with a new 4"C due to troughing on the top and side of the main switch.
there is very little room to safely tap the existing wires, gutter space is limited.
what can be done? any recommendations will be appreciated.

Maybe the electrician can do a tap somewhere downstream of 800A main service switch without additional cost. If the service is 800A, you can't have load higher that 800A on service conductors, what is the point to tap 400A upstream of 800A?
 

victor.cherkashi

Senior Member
Location
NYC, NY
Also another point that bother me for years, I still didn't find an answer. All engineering drawings I saw, also on this post (picture of riser). Engineer doesn't apply tap rules (240.21) for fire alarm disconnect switch. "The tap conductor must be not less than onetenth the rating of the overcurrent device protecting the main feeder to which the tap is being made". WHY #6 (65A@75C) tap is shown on 800A service?
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
Also another point that bother me for years, I still didn't find an answer. All engineering drawings I saw, also on this post (picture of riser). Engineer doesn't apply tap rules (240.21) for fire alarm disconnect switch. "The tap conductor must be not less than onetenth the rating of the overcurrent device protecting the main feeder to which the tap is being made". WHY #6 (65A@75C) tap is shown on 800A service?

The conductors supplying the FA disconnect are service conductors and not tap conductors.
 