Tap Meter Stack Disconnect Box for New Meter Stack

Status
Not open for further replies.

designer82

Senior Member
Location
Boston
Is there any issues with tapping an existing meter stack disconnect box in order to feed a new meter stack?

Is this something electricians routinely do with no problems?

Here are some pics for more clarity:




Thank You
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I think you'd need to start with a good old-fashioned load calc.

Is the box approved for adding load lugs to the busbars?
 

designer82

Senior Member
Location
Boston
Thanks, I ran the load calcs. and loading is not an issue.

As far as your second question, I'm not sure. Any advice on this? Call/check with manufacturer?
 

designer82

Senior Member
Location
Boston
This leads me to a new question. When adding the new branch ring, does it need it's own tap box to connect to or can it be any standard JB?

Please see pic for clarity

 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I would think you're restricted to the manufacturer's approved method(s) of supplying the stack.
 
Status
Not open for further replies.
Top