Can I tap off main lugs of a 400 amp 120/208 panel no main ( 10 ft ) with 000 wire for 200 amp breaker .the load on the service is now is 150 amps, I have no more space in the panel.
The main lugs are rated for more than one wire.
Can I tap off main lugs of a 400 amp 120/208 panel no main ( 10 ft ) with 000 wire for 200 amp breaker .the load on the service is now is 150 amps, I have no more space in the panel.
Ok so the feeder tap rules dont apply. These are service entrance conductors so its a "service tap" which is really adding another set of service conductors. So my aforementioned code reference. Keep in mind you only have 380 amps of conductor (most likely) not 400. Also remember new panel is also a service panel so keep that in mind for your grounding and bonding. IF your lugs are not rated for the two different sized conductors, you could replace them with double hole lugs, or the panel may accept feed thru lugs.YES YES 4 BREAKERS 500KCM 340 AMPS TOTAL
Ok so the feeder tap rules dont apply. These are service entrance conductors so its a "service tap" which is really adding another set of service conductors. So my aforementioned code reference. Keep in mind you only have 380 amps of conductor (most likely) not 400. Also remember new panel is also a service panel so keep that in mind for your grounding and bonding.
IF your lugs are not rated for the two different sized conductors, you could replace them with double hole lugs, or the panel may accept feed thru lugs.