In a inspectors meeting we had,we were told by the chief building inspection that NEC tap rule allows that you can come off of a #12 gage wire with a 20amp breaker or a #14 gage wire with a 15 amp breaker feeding to a light switch and from the light switch to a junction box in the attic to feed lights with a #16 gage wire as a fixture wire as long as I don't exceed over 50 ft.
My question is ,once I put that#12 with 20amps or that #14 with 15 amps to that junction box can I run # 16 gage wire to light fixtures if I follow tap rule?:?