Aaahhhh thank youThe new conductors are the same size (350) so there is no tap.
But there was a tap there before being demolished(see pic).So is there a distance limitation for that tap box from the panel it's feeding?The new conductors are the same size (350) so there is no tap.
The existing has #2/0 being "tapped" off #350 riser. Is that a tap?Look at the definition of a tap (240..2)
In the "existing" you had conductors with an ampacity less than the feeder.
In the new you are just extending the same size feeder (same ampacity)
The existing has #2/0 being "tapped" off #350 riser. Is that a tap?
According to you drawing that is being removed and replaced by the 350s. Now you simply have a splice and no more tap.The existing has #2/0 being "tapped" off #350 riser. Is that a tap?
I completely understand that . Here is my point . I’m trying to determine the location of the existing tap box as it affects my new conduit feeder extension footage to the new location of panels. Soooooo if the existing is considered a tap would the tap box have to be within a certain distance of the panel it’s feeding ?? If so then I know about where the tap box is and I can scale my footage from there to the new panels .According to you drawing that is being removed and replaced by the 350s. Now you simply have a splice and no more tap.
If the tap conductors are 1/3 or larger than the ampacity of the feeder then the tap conductor is limited to 25' in length.I completely understand that . Here is my point . I’m trying to determine the location of the existing tap box as it affects my new conduit feeder extension footage to the new location of panels. Soooooo if the existing is considered a tap would the tap box have to be within a certain distance of the panel it’s feeding ?? If so then I know about where the tap box is and I can scale my footage from there to the new panels .
Ok so 1/3 larger than the #350? Wtf. How do you determine 1/3 of #350 as it relates to wire size ? OD?
So the 2/0 conductors are larger so the box SHOULD be within 25' of panel....regarding existing setup. Question answered. BTW what code section is this in about 1/3 or larger?If the tap conductors are 1/3 or larger than the ampacity of the feeder then the tap conductor is limited to 25' in length.
That's correct. The feeder ampacity would be determined by the OCPD not the conductor size as I think I mentioned in post 11.I hate to confuse the already confused but technically I believe it's 1/3 of the ampacity of the overcurrent device protecting the feeder being tapped (likely the same as the feeder conductor ampacity but not necessarily)
Beau, This is in 240.21