Your math is correct and the maximum size overcurrent is 166.7. there is no overcurrent device listed in 240.6 that matches this so by the rule in 240.21(B) look for the next lowest which is a 150 amp.
Ok, you came up with 150a, the last question came from EC Magazine, and they state it would be (d) 175a OCPD, which is sizing up from 166.7a
What is the correct standard. There are differnt answers from different sources.
400a OCPD /10 = 40a, but can be protected by #8 45a OCPD? (sizing up)
400a OCPD X .33333 = 133a, but must be #1/0 125a (size down)
500a OCPD X .33333 = 167a, but must be #2/0 175a (size up)
Some of you said that 50a or less OCPD is code compliant to protect 400a 10ft. OCPD because #8 has an ampacity of 50a. This is sizing up when other posts stated I have to size down.
I am not the only one confused here.
If #1/0 has an 75 deg. ampacity of 150a, Why do I have to size down to 125a OCPD and not be permitted to use 150a OCPD?
Looks like some want to size down once you come up with the ampacity after dividing. This is where I select my wire size based on that ampacity.
I.E. 400a OCPD X .33333 = 133a, but must be #1/0
Can someone tell me if what should be used, is the ampacity of the wire you selected (not ampacity from division) and size down to the proper OCPD?