cpal

Senior Member
Location
MA
2/0 Cu is needs to be protected at not moer than 175A, if the second panel has 150 A ocpd then 1/0 Cu is ok. (75Deg).are you using Al or Cu??
 

raider1

Senior Member
Staff member
Location
Logan, Utah
they conductors would be 2/0 al. Can you please explain the 200amp tap rule

You could not use 2/0 AL conductors and meet the tap rules. 240.21(B) states the provisions of 240.4(B) (The next size up rule) shall not be permitted for taps. 2/0 AL has an ampacity of 135 amps at 75 degrees C so to meet the tap requirements the 2/0 wires must terminate in an overcurrent device with an ampacity equal to or less than the ampacity of the wires.

The reason that I asked what size the conductors are is if you used conductors rated at 200 amps you would not have a tap at all.

Take a look at 240.21(B)(1) through (5) for the feeder tap rules.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
they conductors would be 2/0 al. Can you please explain the 200amp tap rule

You would need a conductor with an ampacity of not less than 150 amps. Since you mentioned aluminum you would need at least a #3/0 aluminum. Since your tap conductors are more than 1/3 the ampacity of the 200 amp panel you can use the 25' tap rule {240.21(B)(2)}. This will limit your tap conductors to 25' in length.
 