SERVICE TAPSure why not if you can meet the tap rules? I dont really have any idea what you want to do, but are you talking a feeder tap or a "service tap"?
So you are splitting up the 2500 shown into two smaller or using that and another? You are free to tap the service conductors to different service enclosures as long as A. they are grouped B. The number of service disconnects does not exceed 6 C. the conductors serving each main are sized to that main (or to the load if a MLO with multiple service disconnects) D. The length of service conductors does not exceed that allowed by your AHJ. Did I leave anything out anyone?