I'm looking at at a couple of MCC feeder applications and I was wondering where the condtions of the "tap rule" would be applicble in these scenarios.
The first scenario involveds a 500MCM cable which is fed from an upstream 600A feeder breaker and terminates on a 400A main breaker on the downstream MCC. Obviously the 600A feeder breaker does not adequately protect this cable however could the tap rule be applied since the cable terminates in to a single OCPD and therefore the the 400A main breaker in the MCC will adequately protect the feeder cable?
The second scenario is similar to the first however we now have (2) 500MCM cables fed from a 1200A breaker and terminate into a 1000A main breaker in the MCC. Even if the tap rule were to be applied in this case the 1000A main breaker in the MCC would not adequatley protec tthe feeder cable. However if the MCC main breaker was an 800A breaker then with the tap rule applied the breaker would adequately protect the cables is this correct?
The last scenario is a case where a 600A feeder breaker feeds a MLO MCC and then off of the MCC bus there is a 500MCM cable tapped (no OCPD) that then feeds another downstream MCC with a 400A main breaker. In this case the tapped feeder from the MCC is not protected by the upstream 600A breaker, however can it be considered protected by the 400A main breaker in the downstream MCC which it feeds?
Thanks
The first scenario involveds a 500MCM cable which is fed from an upstream 600A feeder breaker and terminates on a 400A main breaker on the downstream MCC. Obviously the 600A feeder breaker does not adequately protect this cable however could the tap rule be applied since the cable terminates in to a single OCPD and therefore the the 400A main breaker in the MCC will adequately protect the feeder cable?
The second scenario is similar to the first however we now have (2) 500MCM cables fed from a 1200A breaker and terminate into a 1000A main breaker in the MCC. Even if the tap rule were to be applied in this case the 1000A main breaker in the MCC would not adequatley protec tthe feeder cable. However if the MCC main breaker was an 800A breaker then with the tap rule applied the breaker would adequately protect the cables is this correct?
The last scenario is a case where a 600A feeder breaker feeds a MLO MCC and then off of the MCC bus there is a 500MCM cable tapped (no OCPD) that then feeds another downstream MCC with a 400A main breaker. In this case the tapped feeder from the MCC is not protected by the upstream 600A breaker, however can it be considered protected by the 400A main breaker in the downstream MCC which it feeds?
Thanks