A colleague and I are having a disagreement concerning the tap rule (see 2002 NEC 240.20). We are working on a project where we have a distribution panel with a 225 Amp branch breaker. From this breaker we are feeding a 225 Amp MLO Panel (three phase, four wire) with #4/0 feeders. At the first panel we are tapping off and feeding a small panel beside the 225 amp panel. This second panel is a 100 amp MLO panel. My colleague argues that the tap rule allows him to have size #3 feeders (taps of less than ten feet) to the 100 amp panel with no overcurrent protection other than the 225 amp breaker in the distribution panel that is protecting the large feeder. My argument is that the 100 amp panel needs to be equipped with a main circuit breaker to protect the taps per NEC 240.21.B.1.1.a (sorry that I haven't used proper punctuation in the reference, but they keep changing it on me). Am I wrong or do I need to insist on a change in the design. Let me thank all who answer in advance.