Hello guys first time poster here thank you in advance for any information.
I have a commercial set up in a shopping center and they are trying to add a 400 amp 480 volt service onto an existing 3000 amp service. The architect is drawing the plans calling for me to set the CT cabinet and feed off the busway with 600 copper to the CTs. All good. He is then making me set two 200 amp fused disconnects to run the secondaries into the space. My issue is he is saying I will have to run 600s to each disconnect. I was wondering why I could not run paralell 3/0 from the CTs to each disco seeing as they are under 10 feet away from the CT cab and will be fused as such at that point.
I have a commercial set up in a shopping center and they are trying to add a 400 amp 480 volt service onto an existing 3000 amp service. The architect is drawing the plans calling for me to set the CT cabinet and feed off the busway with 600 copper to the CTs. All good. He is then making me set two 200 amp fused disconnects to run the secondaries into the space. My issue is he is saying I will have to run 600s to each disconnect. I was wondering why I could not run paralell 3/0 from the CTs to each disco seeing as they are under 10 feet away from the CT cab and will be fused as such at that point.