Tap rule question

Status
Not open for further replies.

ADub

Senior Member
Location
Midwest
Occupation
Estimator/Project Manager
50 amp welder receptacle in corner of garage fed with 6/2 nm, I'd like to tap off of it for a 240v 20 amp fused circuit in the opposing corner of garage. I haven't found anything stating this is an approved tap and I'd like to confirm my doubts here


Sent from my iPhone using Tapatalk
 
If you put overcurrent protection at the welder receptacle end you would not have a tap in the NEC sense at all. Just a run of wire which is simultaneously part of a feeder and a branch circuit.
 
If you put overcurrent protection at the welder receptacle end you would not have a tap in the NEC sense at all. Just a run of wire which is simultaneously part of a feeder and a branch circuit.

No I was planning on putting the ocp at the end of the run. It's over 25' so it's a no go


Sent from my iPhone using Tapatalk
 