Hello,
We have a 62.5 Kva UPS with a 1200 amp DC breaker that feeds a bank of 1200 amp-hour batteries (120) volt DC via a 700 amp disconnect. There is a DC panel tapped off of the UPS side of the DC disconnect that has a 100 amp main. Can you please tell me what size wire I need from the DC panel to the disconnect? IF I use the tap rule at less than 25 feet it seems we need 1200/3 (400 amp wire) 250 kcmil. If we mount the panel within 10 feet of wire we can go down to 120 amp wire or #2 wire. Am I correct in this? The engineer on site told us we had to use 350 kcmil cable and that size will not fit in the 100 amp breaker.
Thanks for your help,
We have a 62.5 Kva UPS with a 1200 amp DC breaker that feeds a bank of 1200 amp-hour batteries (120) volt DC via a 700 amp disconnect. There is a DC panel tapped off of the UPS side of the DC disconnect that has a 100 amp main. Can you please tell me what size wire I need from the DC panel to the disconnect? IF I use the tap rule at less than 25 feet it seems we need 1200/3 (400 amp wire) 250 kcmil. If we mount the panel within 10 feet of wire we can go down to 120 amp wire or #2 wire. Am I correct in this? The engineer on site told us we had to use 350 kcmil cable and that size will not fit in the 100 amp breaker.