Yes.Can I come directly off of a main breaker of a greater amperage value than the wire is rated as long as it lands on the proper breaker downstream? In this case everything is underground.
This seems like a tap without the actual physical tap itself.
While the language in 240.21(B) implied a connection to a feeder conductor, the definition of tap conductor has never addressed the point of connection of the tap conductor. There was never any intent to prohibit a tap from originating at the load terminals of an OCPD, but the language in 240.21(B) in the 2017 and older codes seemed to prohibit that.Can I come directly off of a main breaker of a greater amperage value than the wire is rated as long as it lands on the proper breaker downstream? In this case everything is underground.
This seems like a tap without the actual physical tap itself.