mshields

Senior Member
Location
Boston, MA
A colleague of mine has a 1600A feeder from a 1000kW generator (@480V)protected by a 1600A breaker at the generator. We are informed that the new 2008NEC will require that the switchboard this feeds must have barriered sections for Article 700 loads, 701/702 loads and a separate enclosure for a fire pump OCP if required (which happens to be the case on this project). Problem is that GE, Square D, etc don't make, in switchboard construction a switchboard with full barrier between sections.

This leaves the option of comming to a wire way and tapping in accordance with Article 240. If he does this, does he have to tap each conductor of the 4 conductors in the 1600A feeder OR may he, for example, for a 400A tap, just tap 1 set of conductors?

One manufacturer suggested 3 single section switchboards. But these would not have a common bus and as this is true, we have the same quandry as we have with the wireway to separate devices in NEMA 1 enclosures.

Any thoughts would be appreciated?

Mike
 
Mike,
If he does this, does he have to tap each conductor of the 4 conductors in the 1600A feeder OR may he, for example, for a 400A tap, just tap 1 set of conductors?
You have to connect to all of the conductors of the parallel set to make a tap. If you don't, you have a violation of 310.4.
Don
 
Mike,

you have to specify switchgear not a switchboard. Sq. D, CH etc. make them with barriers.

Weren't you at the last Milton CAT 2008 code update seminar in Newton? I met some of your buddies from SEI.
 