Trip, I don't see anything to prohibit the tap rules in 240.21 from being used but it doesn't seem right to me.Can you splice #2 to the 4/0 alum. so it can fit in 100 amp. main in trailer, considered a tap?
The conductors Trip wants to tap are not service conductors, they are feeders, tap away.Originally posted by trip:
Mobile Home is moved onto an existing site--Service Equipment on pole--200 amp. Disconnect-4/0 out of feed-thru lugs in conduit to trailer panel--can you splice #2 to the 4/0 alum. so it can fit in 100 amp. main in trailer, considered a tap?
Not to often. as most newer trailers will have a 200 main. We have a few trailer parks that has all new service equipment, and the service breakers to the trailers are 200 amps we have done it both ways leave the 200 amp main and run 3/0 copper to a 100 amp fused trailer disconnect then 3 insulated #3 conductor 1 #6 insulated grounding conductor into the trailer. The state HUD AHJ requires the disconnect to be no closer than 2' to the trailer and at least 2' off the ground.By Charlie: Wayne, is this something that is done on a regular basis in northern Indiana?