sparkyand1
Member
- Location
- Paden, OK
We have a situation where we are having to parallel two 1/0 conductors from a 3 phase 120/208 breaker in our switch gear and tap them to feed two disconnects. We have done our due dilligence in the code and we're just not sure if we're interpreting the tap rule correctly. We have a dishwasher @ 50 FLA and a 54 KW booster heater @ 150 FLA. We're considering them both continuous loads. We have two 1 1/4 conduits that we are paralleling 1/0 conductors through. Phase A, B and C in one and A,B and C in the other for a total of 300 amps. We've decided to go with a 250 amp breaker in the main switch gear to feed our paralled 1/0 conductors. The run is about 50 ft. We are going to terminate our 1 1/4 pipes in a gutter above the disconnects. from the gutter we are going to leave with a 2" conduit and about a 3 ft. run into the 200 amp disconnect from there we will use a chase nipple into the 100 amp disconnect. The 200 amp disconnect will power the booster heaters and will have 200 amp fuses. The 100 amp disconnect will have 70 amp fuses in it for the dishwasher. The main question we have is in reference to the tap rule. We are wanting to tap the paralled 1/0 conductors in the gutter with 3/0 and #3 conductors. the 3/0 will power the 200 amp disconnect and the #3 conductors will power the 100 amp disconnect. Everything we've seen in the code will allow us to do this, but everyone I've talked to just aren't sure about the tap rule. Please help.
Thank You
Thank You