FYI, some utilities would now consider this a 260A service ( I have come across this in Western Mass). So either the feeders would need to be upsized to carry 260A or a 200A main disco breaker would need to be installed ahead of the solar tap conductors.
Really? The current flow options are pretty simple. The max current that can flow back at the utility is 60 A. And the max current that can flow to the loads is 200 A.
What's the 260 A scenario? (Dude reverse wires his PV inverter to illuminate the modules at night?)
The PV system isn't a load. If there is a fault and reverse currents flow to the PV inverter, it will be a short duration event that clears the fuses in ac disconnecting means.
I don't understand that interpretation. (Not to say it doesn't happen.) :slaphead:
If you put the 200 A main breaker ahead of the POI for the PV system, it's no longer a supply side interconnection and fall under the 120% rule. Supply side connections are clearly allowed by Code, and are limited only by the rating of the service.