We are reviewing a set of drawings for a client.
They have a 800 amp CB on the incoming service which feed a transfer switch. The transfer switch is also fed by a 600KW generator with an 800 amp CB on its output.
On the load side of the transfer switch is:
1. 500 MCM cables, one per phase, feeding a MCC
and
2. 6-3/0 cables, two per phase, feeding a 250 HP VFD.
I believe this is OK but wanted to get others opinions. It seems as if this installation is two tap conductors with no feeder conductor.
Any comments? Thanks.