Tap rule

Status
Not open for further replies.
Would someone please direct me to the "tap rule" stuff. I'd like to see if the existing vav stuff in this remodel are legit. 45amp ckt feeding multiple 15amp vav's however one branches off the #8 wire and shoots out 200' to a fused disc. I know the conductors should never see more than 15amps cause the fuse will pop. But the 200' has me questioning it.

Sent from my SCH-I545 using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Would someone please direct me to the "tap rule" stuff. I'd like to see if the existing vav stuff in this remodel are legit. 45amp ckt feeding multiple 15amp vav's however one branches off the #8 wire and shoots out 200' to a fused disc. I know the conductors should never see more than 15amps cause the fuse will pop. But the 200' has me questioning it.

Sent from my SCH-I545 using Tapatalk

generally you cannot run a tap this far before terminating it at an OCPD. the sole exception I an aware of is if it is outside.

240.21
 

iwire

Moderator
Staff member
Location
Massachusetts
Would someone please direct me to the "tap rule" stuff. I'd like to see if the existing vav stuff in this remodel are legit. 45amp ckt feeding multiple 15amp vav's however one branches off the #8 wire and shoots out 200' to a fused disc. I know the conductors should never see more than 15amps cause the fuse will pop. But the 200' has me questioning it.

Sent from my SCH-I545 using Tapatalk

What size wire is being used for the 200'?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Is 15 the fla of the motor? The ocpd can be 250% rounded up to the next std size cb. I got the impression that the cb at the end of the 200 foot run was what was 15 amps.
 
Its a vav 15amp is what its fused at. Im fairly certain its due to the heat strips, 480v, at this point i have already pulled out the 10's and pulled in 8's to accomodate the 45amp breaker feeding the circuit. I was wantig a reference so i could read up on it so i the future i can make a more effective choice based on fact not gut. I suspect that 200' is too far but i dont know for sure.

Sent from my SCH-I545 using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Other than conductors outside the building, the tap rules (240.21) normally require conductors longer than 10 ft or 25 ft to be protected at a level no greater than their ampacity,
 

Carultch

Senior Member
Location
Massachusetts
Would someone please direct me to the "tap rule" stuff. I'd like to see if the existing vav stuff in this remodel are legit. 45amp ckt feeding multiple 15amp vav's however one branches off the #8 wire and shoots out 200' to a fused disc. I know the conductors should never see more than 15amps cause the fuse will pop. But the 200' has me questioning it.

Sent from my SCH-I545 using Tapatalk


240.21(B) is the set of tap rules.
240.21(C) is a set of analogous rules for transformer secondary conductors.

A tap is a section of conductors that are protected, except only in excess of their ampacity. They do not get protected against overload, until terminating at an overcurrent device on the opposite end of the tap point.

The only case when you can tap a 200 ft of 1-way circuit distance from tap point to overcurrent device, is with an outside unlimited tap rule. 240.21(B)(5).

Indoors, you have to terminate within 10 ft or 25 ft of the tap point. Unless you can apply the very obscure 100 ft tap rule.
 

kwired

Electron manager
Location
NE Nebraska
240.21(B) is the set of tap rules.
240.21(C) is a set of analogous rules for transformer secondary conductors.

A tap is a section of conductors that are protected, except only in excess of their ampacity. They do not get protected against overload, until terminating at an overcurrent device on the opposite end of the tap point.

The only case when you can tap a 200 ft of 1-way circuit distance from tap point to overcurrent device, is with an outside unlimited tap rule. 240.21(B)(5).

Indoors, you have to terminate within 10 ft or 25 ft of the tap point. Unless you can apply the very obscure 100 ft tap rule.

Keep in mind you may be able to create the equivalent of outdoor conductors by encasing a raceway or cable (if permitted to be encased) in at least 2 inches of concrete and then use the outside taps of unlimited length rule.
 