OldTiredEngineer
Member
- Location
- Indianapolis
I have a 800Amp CB for a 480VAC System. On the load side of the breaker, the only lug size they offer is 2-500MCM connections per pole. After the 800Amp CB, there are four 200Amp fuse blocks. So I took 1-500MCM to a distribution block rated for 760Amps. The load side i have 3/0 wire going to two of the 200amp fuse blocks. I took another 1-500MCM to a second distribution block and have 3/0 wire going to the other two 200amp fuse blocks.
I guess this is the first time I have ever had to split the load side of a circuit breaker into two separate distribution blocks.
The corporate engineer for the company we are working for is saying this is a violation of the tap rule. While I can kind of understand his point, I disagree. So I'm looking for another opinion.
I guess this is the first time I have ever had to split the load side of a circuit breaker into two separate distribution blocks.
The corporate engineer for the company we are working for is saying this is a violation of the tap rule. While I can kind of understand his point, I disagree. So I'm looking for another opinion.