The language in many of the tap rules (240.21(B)(3) to be exact) includes the requirement:
"The secondary conductors terminate in a single circuit breaker or set of fuses that limit the load current to not more than the conductor ampacity that is permitted by 310.15."
I assume this means I can't use 240.4(B) which allows the next higher standard overcurrent device. But, can I use the 90C column of table 310.15? This would allow #1 to be terminated in a 150A breaker. What if the breaker the wire terminates in is only rated 75C?
STeve
"The secondary conductors terminate in a single circuit breaker or set of fuses that limit the load current to not more than the conductor ampacity that is permitted by 310.15."
I assume this means I can't use 240.4(B) which allows the next higher standard overcurrent device. But, can I use the 90C column of table 310.15? This would allow #1 to be terminated in a 150A breaker. What if the breaker the wire terminates in is only rated 75C?