For overcurrent protection purposes (Art 240 stuff) a connection is not a tap. A tap only occurs when the 'new/added' conductor is smaller than the protective device.
For all but a few instances taps are limited to 25' of conductor length
To be compliant, you need to provide 1600A worth of conductor all the way to the furthest disconnect switch. Or, all of your 200A and 100A disconnect connections need to be made with (2) 600kcmil and not exceed 3' to the furthest switch