Loads permitting, you can tap the 50 amp circuit as desired and feed an overcurrent protective device. 210.19(A)(3) refers to specific appliances
that can be tapped from a 50 amp branch circuit without additional overcurrent protection. I don't see the microwave fitting into the allowable appliances. From the info given, the oven is questionable.