I don't have my code book in front of me at the moment and I am trying to clear up a "tap rules" question.
I'll be tapping off the service entrance conductors(not feeders) of a residence to supply a small 100 amp panel for a solar back-feed combiner. I am wondering if I can land the tap conductors on the main lugs of this panel or do I have to land on a breaker? The tap will be less than 10 feet.
The only advantage I see to the main breaker is being able to de-energize the bus bar of the 100 amp panel. But it's a solar combiner that will have a sticker saying "Solar combiner Only". So the idea is nobody will be working in it anyway.
Thanks