Scenario is installing factory-assembled electronic meter enclosures. Much like most industrial control panels, they have an internal fused disconnect with FNQ-R Class CC fuses rated at 200KAIC which covers almost all possible install locations. They also have an internal shorting block. We know from NEC 230.82 that a meter or meter disconnect is allowed to be connected to the supply side of a service disconnect. Being a second meter in addition to any existing utility meter, the meter enclosure could be immediately adjacent to a main switchboard or up to 25 feet or so (in conduit/wiring) away, depending on wall space. I have had several locations where someone will insist that the meter installation has to comply with 240.21 tap rules, in some cases wanting to require a voltage fuse block and sometimes a CT shorting block in or attached to the switchboard enclosure. I have always contended that metering, by virtue of its being addressed in 230.82, is not technically a branch circuit and therefore not subject to tap rules. Am I correct?