dummycheck
Member
- Location
- Texas
- Occupation
- Engineer
Working on a project where I have a few interesting situations at play and hoping to get some guidance. I'm looking to add load to an existing service entrance.
Existing conditions are 480V 800A service entrance, main lug only, (5) disconnects existing. The AHJ has agreed to grandfather us in to the having the 'six disconnect rule' and allow us to add another disconnect.
The problem is that the breaker size we want to install will not fit within the existing enclosure. So we're looking at tapping off the service entrance bus and installing a separate enclosure disconnect switch adjacent to the service entrance enclosure. We might be able to get it within 10 ft, but it could be tight. I think I would consider this "grouped" with the other disconnects, although I guess that'll be up to the AHJ.
The question I have is that the tap rules don't really talk about tapping off a service entrance, but it doesn't seem like this is a "shall not" type of situation. Do you think this will be allowed under the NEC? What things to I need to consider here?
Existing conditions are 480V 800A service entrance, main lug only, (5) disconnects existing. The AHJ has agreed to grandfather us in to the having the 'six disconnect rule' and allow us to add another disconnect.
The problem is that the breaker size we want to install will not fit within the existing enclosure. So we're looking at tapping off the service entrance bus and installing a separate enclosure disconnect switch adjacent to the service entrance enclosure. We might be able to get it within 10 ft, but it could be tight. I think I would consider this "grouped" with the other disconnects, although I guess that'll be up to the AHJ.
The question I have is that the tap rules don't really talk about tapping off a service entrance, but it doesn't seem like this is a "shall not" type of situation. Do you think this will be allowed under the NEC? What things to I need to consider here?