I am a residential electrician who has the chance to do a very straight forward commercial job, but I have a question that I could kindly use some input on.....
A large building is divided into 5 office/warehouse spaces. The main service is 800 amp 120/208v three phase four wire terminating into a 800 amp main breaker panelboard (just with the one 800 amp main breaker). To the right of this panel is a very typical inter-connecting gangable metering system (with 100 main breaker with each meter) that are connected to the main panel load side busbars for the single phase power to each office subpanel for general lighting/use.
To the left of the panel is an enclosure that is also connected to the main panel load side busbars which have terminal lugs for cable that is feeding (thru a very large gutter and with 6' in distance from main panel) a 400 amp "termination box" to provide three phase 4 wire power to any office that requires a three phase panel. Two office/warehouses have existing three phase 200 amp services from the lugs in the termination box, into a meter socket, into a fused main disconnect, and running quite a distance into the panel located in their offices.
The office directly on the other side of the electrical room will now need a three phase service for a small three phase motor. I understand the need for the disconnects on the existing three phase services due to the distance between the meter socket in the electrical room and the panel inside the offices. But if i wanted to install a new meter an additional 6' from that termination box (so roughly 12' total from main panel), can I simply go "back to back" from the meter socket and straight into a main breaker panel directly behind it on opposite side of the same wall? so meter inside electrical room and panel located on otherside of electrical room wall......or is there an issue of since I am using that tap to feed my new meter socket, will I need a fused disconnect prior to leaving the electrical room and into the panel in the office?
For some reason I was concern about doing this without the fused disconnect?!?!
Any input will be very helpful.
A large building is divided into 5 office/warehouse spaces. The main service is 800 amp 120/208v three phase four wire terminating into a 800 amp main breaker panelboard (just with the one 800 amp main breaker). To the right of this panel is a very typical inter-connecting gangable metering system (with 100 main breaker with each meter) that are connected to the main panel load side busbars for the single phase power to each office subpanel for general lighting/use.
To the left of the panel is an enclosure that is also connected to the main panel load side busbars which have terminal lugs for cable that is feeding (thru a very large gutter and with 6' in distance from main panel) a 400 amp "termination box" to provide three phase 4 wire power to any office that requires a three phase panel. Two office/warehouses have existing three phase 200 amp services from the lugs in the termination box, into a meter socket, into a fused main disconnect, and running quite a distance into the panel located in their offices.
The office directly on the other side of the electrical room will now need a three phase service for a small three phase motor. I understand the need for the disconnects on the existing three phase services due to the distance between the meter socket in the electrical room and the panel inside the offices. But if i wanted to install a new meter an additional 6' from that termination box (so roughly 12' total from main panel), can I simply go "back to back" from the meter socket and straight into a main breaker panel directly behind it on opposite side of the same wall? so meter inside electrical room and panel located on otherside of electrical room wall......or is there an issue of since I am using that tap to feed my new meter socket, will I need a fused disconnect prior to leaving the electrical room and into the panel in the office?
For some reason I was concern about doing this without the fused disconnect?!?!
Any input will be very helpful.