. Are the load side terminals listed such that the additional cables can be terminated there. I would venture to say that they are probably not listed for more than one cable for each terminal.taping a off the load side of the main service disconnect
if provided with service equipment and installed in accordance with requirements for service-entrance conductors .
Where are they permitted?240.3(3) Tap Conductors. As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4.
And (E) directs us to 240.21240.4 Protection of Conductors.
Conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.15, unless otherwise permitted or required in 240.4(A) through (G) .
And 240.21(B)(5) Allows it.(E) Tap Conductors. Tap conductors shall be permitted to be protected against overcurrent in accordance with 210.19(A)(3) and (4), 240.5(B)(2), 240.21 , 368.11, 368.12, and 430.53(D).
As long as it meets the (1) through (4)(5) Outside Taps of Unlimited Length. Where the conductors are located outdoors of a building or structure , except at the point of load termination, and comply with all of the following conditions:
I have to start reading these things with my glasses on. I thought that it said the line side of the service disconnect.taping a off the load side of the main service disconnect