Tap rules

Status
Not open for further replies.

ohmhead

Senior Member
Location
ORLANDO FLA
10 foot tap rule on secondary side of transformer unprotected feeder . Can be used in any space or building correct .

25 foot is only aloud in a industrial location is that correct? Or can you run less then 25 foot and still be unprotected any place ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The general 10' or 25' can be run in any location. The 25' industrial rule is for switchboards and switchgear and more than one OCPD.
 

ohmhead

Senior Member
Location
ORLANDO FLA
tap rule

tap rule

The general 10' or 25' can be run in any location. The 25' industrial rule is for switchboards and switchgear and more than one OCPD.


So in a commercial building you can run 25 foot or less yes /no from a transformer secondary in fused?
 