Here is the situation. I have 3 #1 CU conductors tapping off of 6 250 kcmil AL conductors. The 6 250's are fused at 350 amps. The #3's are going to a 90 amp disconnect. The distance between the tap and the disconnect is less than 25'. At this point I see no problem, due to the 25' tap rule. Let me know if you do. At the load side of the 90 amp disconnect three #4's and three #10's come off and go to a heat pump about 35' feet away. The #10's land on a contactor and the #4's go to a set of 45amp fuses. The #10's are for the compressor and fan. The #4's are for the heat strips. This is a definate violation of the tap rules, right? My question is how to fix the situation. One thought was set a disconnect at the unit and use the ten foot tap rule. So I would have a fused disconect within 25' of the 6 250's then come off the load side of that disconnect and go about 35' and set a disconnect on the heat pump itself. The disconnect would need to be fused, right? Is this considered tapping a tap? Any suggestions would be appreciated.
Thank you
Tim