Tap to bus

Status
Not open for further replies.

Shockedby277v

Senior Member
Location
Michigan
I am installing numerous meters for panels currently. An issue I keep running into is panels that are fully loaded with no space to feed the meters. Through RFI’S we have added a sub-panel and adjusted feeds around to provide a feed for the meter from the panels. Is it acceptable to tap directly onto the buss for a feed to the meter that has a disconnect and fuses for overcurrent protection? This would be like how the factory does it when they install them but again that is factory installed. I am not a huge fan of the idea but I am also not a huge fan of adding sub-panels everywhere either if it can be avoided.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We tap the bus or use an insulation piercing connector to connect the tap conductors to the panel. From there we feed a disconnect switch using the 10' tap rule.
 