Tapcons

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Tapcons have a pretty impressive pullout strength, depending on size, and 5 or 6 in a section of Unistrut can support a pretty impressive load. However, you should be mindful of the customer requirements, if any. The Port Authority of NY/NJ will not allow Tapcons or drop-in anchors or anything else to attach an overhead load to a concrete ceiling. The support would have to be cast-in during the pour.
 

garbo

Senior Member
Not a big fan of Tapcons. Even using thier drill bits usually have problem with some stripping out or not holding. I'm old school and like using 1/4 & 3/8" lead anchors set by the Greenlee tool that threads into it before setting the anchor. Have installed 3/8" lead anchors in ceilings and tied pulling block to it to pull cable up to 4/0 copper. Several times I installed two 1/4" lead anchors to mount a piece of unistrut in a ceiling to hoist a drive weighting over 150 #'s.
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
Some anchors like the "lead nail ins" are not approved for overhead use. Not a fan of Tap Cons myself. They seem to be hit or mis with me. Sometimes good results sometimes not so good.

For concrete I like the steel drop ins

For Block & Brick the block anchors are good

The sleeve type anchors are pretty good for concrete or block but the stud size is smaller than the drilled hole

I dislike the sleeve stud anchors with the small sleeve they just seem to creep when you tighten them.
 

JJWalecka

Senior Member
Location
New England
What do the installation instructions for Tapcons say?

R

Some anchors like the "lead nail ins" are not approved for overhead use. Not a fan of Tap Cons myself. They seem to be hit or mis with me. Sometimes good results sometimes not so good.

For concrete I like the steel drop ins

For Block & Brick the block anchors are good

The sleeve type anchors are pretty good for concrete or block but the stud size is smaller than the drilled hole

I dislike the sleeve stud anchors with the small sleeve they just seem to creep when you tighten them.
I was always under the assumption in a fire ALL the overhead lead anchors would fail. Im not a big fan
 

JJWalecka

Senior Member
Location
New England
Not a big fan of Tapcons. Even using thier drill bits usually have problem with some stripping out or not holding. I'm old school and like using 1/4 & 3/8" lead anchors set by the Greenlee tool that threads into it before setting the anchor. Have installed 3/8" lead anchors in ceilings and tied pulling block to it to pull cable up to 4/0 copper. Several times I installed two 1/4" lead anchors to mount a piece of unistrut in a ceiling to hoist a drive weighting over 150 #'s.
Appreciate your input
 