tapered to straight threads. NPT to NPS

Status
Not open for further replies.

Nick.P

Member
Location
washington
Can a fitting [eg. liquid tight (L/T), Flex fitting] attach to a a)coupling, b)threaded hub/boss, c)Conduit body/condulet. In short, can one connect a Tapered thread (NPT) to a Straight thread (NPS*)? I see there are a few articles about this subject dating back to 1997. i have post link to the IAEI and to EC that go in to further detail. There are so many different answers that I have read/heard. mostly overall the answer is NO!! but the industry standard is YES?

I point out that a rigid conduit is NPT and a coupling is NPS, This is okay as it is UL listed 6. so this is good for wet locations and suitable for a low impedance bonding/grounding path. The NEC calls out NPT per ANSI/ASME B.1.B.20.1. The ANSI section states (NPT, NPSC, NPTR, NPSM, NPSL) are covered in this section. so i ask how would one make a raceway connection from a rigid conduit to a motor? no one has yet to answer this question with out combining NPT to NPS somewhere.

There is a few products that go from GRC to LFMC so this can solve some issues from GRC to LFMC but then the hub of the motor/device may have NPS threads.

i don't see why if the NEC says to use ANSI threads and all electrical threads are cut to this standard. this also meets the federal standards H28. why do i need do but another product or re-work any fitting and i still am unable to get a method of connection to a motor from the folks that bring up the issue. the company I work for has talk to UL about this and never tested in wet locations. the NEC states this is good in a Class 1 Div I location and UL article DFWT stays if its is good in a hazardous location is is more than suitable in a ordinary location.

please wise folks from the internet you'r my only hope!!!

There are several thread types ANSI B1.20.1 covered all of these and referred to as NPT:
NPT = National Pipe Thread
*NPS = National Pipe Straight
*NPSC = National Pipe Straight Coupling
*NPSM = Straight Mechanical Pipe Thread


346-8. Reaming and Threading. All cut ends of conduits shall be reamed or otherwise finished to remove rough edges. Where conduit is threaded in the field, a standard cutting die with a 3⁄4-in. taper per foot (1 in 16) shall be used.
FPN: See Standards for Pipe Threads, General Purpose (Inch), ANSI/ASME B.1.20.1-1983.

500-3(d)
Threaded Conduit. All threaded conduit referred to herein shall be threaded with an NPT... Such conduit shall be made wrench-tight to prevent sparking when fault current flows through the conduit system, and ensure the explosionproof or dust ignition proof .... per ANSI/ASME B.1.20.1-1983

501-4. (a)(2) Flexible Connections. Where necessary to employ flexible connections, as at motor terminals, flexible fittings listed for Class I locations shall be used....Where provision must be made for limited flexibility, as at motor terminals, liquidtight flexible metal conduit with approved fittings, ... shall be used.

ANSI/ASME B.1.20.1-1983
1 INTRODUCTION International Assoc. of Elec. Inspectors
1.1 Scope This Standard covers dimensions and gaging of pipe threads of the following series: NPT, NPSC, NPTR, NPSM, NPSL

International Assoc. of Elec. Inspectors

https://iaeimagazine.org/magazine/2012/07/16/transitioning-between-raceways/

Electrical Contractors magazine-

https://www.ecmag.com/section/codes-standards/fittings-hubs

UL Listing –
UL 514b DWTT - Conduit Fittings http://productspec.ul.com/document.php?id=DWTT.GuideInfo
DFWV / AALZ - Electrical Equipment for Use in Ordinary Locations http://productspec.ul.com/document.php?id=AALZ.GuideInfo
KDER - Grounding and Bonding Equipment http://productspec.ul.com/document.php?id=KDER.GuideInfo
UL 6 DYIX - Rigid Ferrous Metal Conduit http://productspec.ul.com/document.php?id=DYIX.GuideInfo

ANSI B1.20.1 –
http://esh-docdb.fnal.gov/cgi-bin/R...ilename=Pages from B1-20-1_2013.pdf&version=6

Federal Standard H28 Machinery's Handbook 27th Edition http://www.nashua.edu/paradisem1/Machinery's Handbook 27th/27_Thread_09A.pdf

Fitting option 1 - https://www.emerson.com/en-sg/catalog/o-zgedney-4q-fm-lt-ozg-en-sg
Fitting option 2 - https://www.bptfittings.com/store/c...b-malleable-iron-body-with-steel-ferrule.html

T&B fitting
http://www.tnb-canada.com/en/pdf-ca...quidtight-flexible-metal-conduit-fittings.pdf


 
I ask a similar question to UL years ago about threading a raintight EMT connector into a weather proof bell box, and saved the reply:
UL Certifies (Lists) Conduit Fittings under the product category for Conduit Fittings (DWTT), located on page 141 of the 2015-16 UL White Book, pdf located at www.ul.com/whitebook and also on UL Product Spec at www.ul.com/productspec and enter DWTT at the category code search field. In the guide information you will find that with or without a gasket/seal, all male threaded fittings and nipples have only been investigated for use with locknuts only and have not been evaluated for use with hubs.

To expand just a little further, even grounding and bonding hubs that are certified and provided with a certified grounding or bonding locknut have not been evaluated for use with conduit fittings. They serve in a manner similar to grounding and bonding bushings except they are only for use with threaded rigid metal and intermediate metal conduit
 
Short answer is no, having said that it's done thousands of times a day without any problems.
 
We found O/Z gadney and TnB make something similar. Now we are trying to find out how to connect to a motor hub.

Silly i know. But if cant mix the threads.…