Is it permissable to tap parallel conductors under any of the tap rules(Found nothing either way)? And if so would you also parallel the tap conductors so as not to overload any one tapped conductor?
when I parallel it I am thinking each individual tap wire will more than likely be less than the minimum 1/3 the size of the OCPD. Or in this instance would the tap conductors total ampacity or individual ampacity be taken? Hope this makes sense
thanks
240.21(C) requires the tap condcutor ampacity to be 1/3 of the 800 amp (267 amps). So your tap would be a 300 kcmil.
On reflection, an argument might made that the tap could not be less than 300 since even if you parelleled 1/0s the "tap conductor" ampacity would be less than 267 (each individual)