Thank your for your reply.
In the UL508A standard I found the information below, it is noted that for grounding it is necessary to refer to section 28.
See point 28.2.3 below, but it doesn't say whether the components must be certified....
14.2 An industrial control panel shall be provided with a field wiring terminal for the connection of an
equipment grounding conductor. The terminal shall comply with:
a) The component requirements of a field wiring terminal in accordance with Section 28, Field
Wiring; or
b) The requirements in the Standard for Grounding and Bonding Equipment, UL 467.
28.2.3 A wire binding screw, other than one on a terminal block or a component, shall comply with the
following:
a) A terminal plate tapped for a wire-binding screw shall be of metal not less than 0.030 inch (0.76
mm) thick for a 14 AWG (2.1 mm2) or smaller wire, and not less than 0.050 inch (1.27 mm) thick for
a wire larger than 14 AWG (2.1 mm2). There shall be at least two full threads in the plate; and
Exception: Two full threads are not required if fewer threads result in a secure connection in which
the threads will not strip upon application of a 20 pound-inch (2.3 N·m) tightening torque.
b) A terminal plate formed from stock having the required thickness specified in (a) is able to have
the metal extruded at the tapped hole for the binding screw to provide two full threads; and
c) A wire-binding screw shall thread into metal; and
d) A wire-binding screw shall be No. 8 (4.2 mm diameter) or larger screw for securing a 10 AWG
(5.3 mm2) or smaller conductor, or a No. 6 (3.5 mm diameter) screw for securing a 14 AWG (2.1
mm2) conductor only.