Member
A building has a 600 amp fused service disconnect. On the load side of the disconnect are parallel lugs with 350mcm feeding a 600 amp main lug panelboard 120/208v. This main lug panelboard is 6ft. away from the service disconnect.
I am taking this job because the other contractor could not finish the job.
He had mounted a 400 amp panel box right next to the service disconnect and intended to put triple lugs in the disconnect and also feed the 400 amp main lug panel with 500 mcm.
I think the 400 amp panel should have a 400 amp main breaker. The buss is rated for 400 amps.
Would the tap rule cover this?
(The load will not change on the service disconnect, it will be a redistribution of power)
600 amp fuses in service disconnect.
Total connected load on 400 amp is 263A
Thanks