New to the forum, so I ask for your patience in advance. Hope I am in the right place, and that this question falls within the TOS guidelines.
We have a 600 amp MDP with ancient breakers, and are adding a 200 amp panel for some mini-split A/C units. My intent is to install a 200 amp disconnect within 10 feet of the MDP, and use it to supply a w/p panel on the roof where the condensers will be located. The MDP is fed from a 600 amp main disconnect, in parallel. My question is, can this be accomplished by tapping one set of those parallel feeders in the MDP, or do the taps need to be in parallel as well? I hope my explanation is clear enough to be understood, and thank you in advance for your help.
We have a 600 amp MDP with ancient breakers, and are adding a 200 amp panel for some mini-split A/C units. My intent is to install a 200 amp disconnect within 10 feet of the MDP, and use it to supply a w/p panel on the roof where the condensers will be located. The MDP is fed from a 600 amp main disconnect, in parallel. My question is, can this be accomplished by tapping one set of those parallel feeders in the MDP, or do the taps need to be in parallel as well? I hope my explanation is clear enough to be understood, and thank you in advance for your help.