This installation violates 240.C2(1)(b). 240.C1, C3, C4, C5 Do not apply.
Violation of 240.C6(2)
 
Through all of this posting the answer is found in 240.21;

240.21 Location in Circuit.
Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (G). No conductor supplied under the provisions of 240.21(A) through (G) shall supply another conductor under those provisions, except through an overcurrent protective device meeting the requirements of 240.4.
 