Suppose we have a reliable source, Can we tap the fire pump directly from owner 13.8kv transformer and ahead of Main distribution panel?
m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Nov 20, 2019 #2 Appreciate your feedback
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Nov 20, 2019 #3 Yes.
m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Nov 21, 2019 #4 charlie b said: Yes. Click to expand... Thanks for your reply, but assuming this transformer is not part of campus and it's located in a single building, can we still supply FP from this transformer ? I am referring to 695.5 & 695.5(c) and t's really confusing me. Last edited: Nov 21, 2019
charlie b said: Yes. Click to expand... Thanks for your reply, but assuming this transformer is not part of campus and it's located in a single building, can we still supply FP from this transformer ? I am referring to 695.5 & 695.5(c) and t's really confusing me.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Nov 22, 2019 #5 695.5(C) does not apply. Your answer lies in 695.3(A)(1).
m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Nov 24, 2019 #6 charlie b said: 695.5(C) does not apply. Your answer lies in 695.3(A)(1). Click to expand... But, it doesn't mention a feeder connection.
charlie b said: 695.5(C) does not apply. Your answer lies in 695.3(A)(1). Click to expand... But, it doesn't mention a feeder connection.
m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Nov 24, 2019 #7 m sleem said: But, it doesn't mention a feeder connection. Click to expand... Or, you meant 695.3(A)(3) ?
m sleem said: But, it doesn't mention a feeder connection. Click to expand... Or, you meant 695.3(A)(3) ?