Hi all, just joined here and happy to have found this forum.
I have a project where a building has (1) 400A, 120/208, 3Ph (400A main circuit breaker) panelboard supplying the space. The existing load is probably ~100A-150A max.
We are installing (2) new HVAC units, totaling in about 75A of load. I would like to tap off the existing 400A feeders to a new subpanel for the mechanical units as the existing panel is completely full and there are no spares or spaces.
Would I be right in that for a new 100A subpanel, I can tap off the existing feeders and use #1's (Table 310.15(B)(16), 60deg column per 110.14(C)) to my new panel? I used the downstream OCPD (100A subpanel) for conductor sizing, conductors aren't extending beyond the equipment they supply, conductors are in a raceway, and the ampacity of the taps meets the 10% rating of the upstream OCPD. (All rules found in 240.21(B)(1) for taps not over 10')
Question: is there anything in the NEC prohibiting me from tapping the feeders before the MCB? The upstream OCPD has not yet been verified, but per 408.36, we know that the upstream OCPD is 400A max... so any breaker smaller would still meet the 10% rating requirement (240.21(C)(1)(4)).