240.5 (B) Fixture wire shall be permitted to be tapped to the branch circuit conductor of a branch circuit according to the following; (3) 20 ampere circuits - 14 AWG and larger.
I have a junction box in the attic with a 20 amp circuit with #12 AWG wire.
Does this mean that I can tap into it with #14 AWG to feed a light switch .
As far as I'm concerned 240.4 Protection of conductors clearly states that:
240.4 (D) (3) 14 AWG Copper - 15 amps
240.4 (D) (5) 12 AWG Copper - 20 amps
Table
310.15 (B) (16) clearly says use #14 AWG for 15 amps ,and #12 AWG for 20 amps.
I have a junction box in the attic with a 20 amp circuit with #12 AWG wire.
Does this mean that I can tap into it with #14 AWG to feed a light switch .
As far as I'm concerned 240.4 Protection of conductors clearly states that:
240.4 (D) (3) 14 AWG Copper - 15 amps
240.4 (D) (5) 12 AWG Copper - 20 amps
Table
310.15 (B) (16) clearly says use #14 AWG for 15 amps ,and #12 AWG for 20 amps.