I ItsHot Senior Member Location A little piece of heaven! Aug 25, 2009 #1 Can a new device be fed from tapping off of a disconnect? For example..exsisting 50 A ciruit with disconnect, can a new 20A circuit be tapped out of the disconnect? Searching for art. in NEC.
Can a new device be fed from tapping off of a disconnect? For example..exsisting 50 A ciruit with disconnect, can a new 20A circuit be tapped out of the disconnect? Searching for art. in NEC.
B bphgravity Senior Member Location Florida Aug 25, 2009 #2 The tap rules for branch circuits can be found in section 240.21(A) which refers you back to 210.19. In general, the scenerio you describe is not permitted.
The tap rules for branch circuits can be found in section 240.21(A) which refers you back to 210.19. In general, the scenerio you describe is not permitted.
I ItsHot Senior Member Location A little piece of heaven! Aug 25, 2009 #3 thanks! thanks! Thanks Brian! I guess if this was permitted, you would have very few "individual" branch circuits.
thanks! thanks! Thanks Brian! I guess if this was permitted, you would have very few "individual" branch circuits.