We are coming up with a common situation with our PV systems where we need to tap on a small wire, just 14 or 12 copper for voltage reference and power for an energy monitor on to the service conductors. The way it almost always works out for us, because we specialize in ground mounts and the way I like to make the interconnection, we have a pull box located on a pedestal under or next to the utility meter. There's no disconnect, panel board or other equipment at the pedestal besides the meter and the box. The conductors in the box are typically 4/0 or 250 aluminum and have connections with h taps. So how to tap on a 12 copper onto these aluminum service conductors? Just hoping maybe there's some slick easy cheap way I haven't thought of or don't know about
. It seems like someone must make like a little clamp like mini insulation piercing thing with a stud or a screw for a ring terminal? Don't utilities have need for such a thing? I tried googling various things but couldn't come up with anything. It's tempting to just put a piece of #12 CU in the h-tap before crimping, and I'm 99.3% certain that wouldn't result in a compromised connection or a failure, but I'm still having trouble bringing myself to do that. Split bolt seems like Overkill and not rated for that smaller wire anyway. Polaris type connectors usually only go down to number six at that size, and granted I could wire nut a 6 tail to a 12 for the monitor, but I don't really want to use Polaris connectors, they're spendy and I love my h-taps. Any other ideas?